Wanderer wrote in message . ..
On Wed, 10 Sep 2003 15:21:57 +0100, Roland Perry wrote: In message , Wanderer writes Finally! Confirmation that the two faults were indeed related. As some of us insisted (against solid opposition) from the start. Not quite true. You conveniently snipped the *real* reason, which was almost certainly human error. The *reason* for the second outage might have been human error [1], but the second outage was most definitely *caused* (ie triggered) by the first. It wasn't an "unrelated" incident. On any interconnected system, the National Grid being a prime example, events are by definition related. This incident was caused by a classic very simple installation 'cock-up' made 2 years ago and not discovered or exposed since; system design, configuration and incident response were correct and supplies would have been securely maintained otherwise. The second outage (Wimbledon - New Cross 275kV circuit No.2) which caused the loss of supply was a 'phantom' overload trip, there was no equipment fault and total load was 33% of line rating. Overload detection relays, connected via 1,200:1 transformer, are rated 1Amp or 5Amp with a wide ranging multiplier, 5A was specified but 1A installed and through all the checks nobody spotted the error. This meant that tripping was initiated (time delay involved, irrelevant here) at 23% of rating and 20% of correct overload setting, so in the past 2 years this line can't have loaded above that level even at peak winter demand indicating the generous level of redunancy provided. It's accepted that when the system is being reconfigured, as it was after the first, potentially explosive, fault warning; there can be 5 to 10 mins 'switching time' when supply is via a single circuit. The risk of a second fault on that circuit during this time is estimated at 1:40,000 though that doesn't apply here with the system wrongly set-up. The engineers planning the switching could not have known the line would trip. [1] Although you could argue that it was really caused by failure to implement a procedure that would have noticed and rectified that human error. Yes. Knowing the very strict and thorough commisioning and testing procedures that once were enforced, one is left wondering whether corners have been cut since privatisation. They were carried out but I guess those engineers assumed they had been handed over correctly installed equipment and never thought to check the relay rating, pity they aren't brightly colour coded. Simulating real life faults is simply not possible or wise. Reading the full report my impression is of a well run and financed operation not obviously damaged by privatisation with London area investment running at £50m pa. Ironically the duplicate circuit, Wimbledon - New Cross No.1, is out from 1/7 to 28/9 for upgrade and refurb. Lessons have been, painfully, learnt and the relay error is not likely to happen again. All 45,000 are being checked (none found after 9,000). I would say the system is now secure, building extra lines would be very expensive. The LT loss of supply is rather laid on EDF, the London distribution operator, who chose to operate their Wimbledon 132kV Substation in a way that resulted in LT and others losing supply when the Grid was able to maintain the full load without interuption, and should have reconnected LT in a couple of mins at most. I get the impression there was only one engineer in their Control who didn't know what hit him... Source: http://image.guardian.co.uk/sys-file...on28082003.pdf |
#12
![]() |
|||
|
|||
![]()
On 10 Sep 2003 15:31:14 -0700, robsignals
wrote in : detection relays, connected via 1,200:1 transformer, are rated 1Amp or 5Amp with a wide ranging multiplier, 5A was specified but 1A installed .... They were carried out but I guess those engineers assumed they had been handed over correctly installed equipment and never thought to check the relay rating, pity they aren't brightly colour coded. Given that there appear to be only two different ratings, an obvious question is, "Why not?" -- Ivan Reid, Electronic & Computer Engineering, ___ CMS Collaboration, Brunel University. Room 40-1-B12, CERN KotPT -- "for stupidity above and beyond the call of duty". |
#13
![]() |
|||
|
|||
![]()
On Thu, 11 Sep 2003 09:48:26 +0000 (UTC), "Dr Ivan D. Reid"
wrote: On 10 Sep 2003 15:31:14 -0700, robsignals wrote in : detection relays, connected via 1,200:1 transformer, are rated 1Amp or 5Amp with a wide ranging multiplier, 5A was specified but 1A installed ... They were carried out but I guess those engineers assumed they had been handed over correctly installed equipment and never thought to check the relay rating, pity they aren't brightly colour coded. Given that there appear to be only two different ratings, an obvious question is, "Why not?" becuase some pratt would probabably colour them red & green them employe colour blind engineers. -- This post does not reflect the opinions of all saggy cloth cats be they a bit loose at the seams or not GSX600F - Matilda the (now) two eared teapot, complete with white gaffer tape, though no rectal chainsaw |
#14
![]() |
|||
|
|||
![]() "Dr Ivan D. Reid" wrote in message ... On 10 Sep 2003 15:31:14 -0700, robsignals wrote in : detection relays, connected via 1,200:1 transformer, are rated 1Amp or 5Amp with a wide ranging multiplier, 5A was specified but 1A installed ... They were carried out but I guess those engineers assumed they had been handed over correctly installed equipment and never thought to check the relay rating, pity they aren't brightly colour coded. Given that there appear to be only two different ratings, an obvious question is, "Why not?" The cost of producing the item? Perhaps they aren't made? You'd hope that the maintenance engineers actually bothered to read things. Perhaps if the correct colour code was yellow they might stuff a banana in by mistake. |
#15
![]() |
|||
|
|||
![]()
W K wrote:
"Dr Ivan D. Reid" wrote in message ... On 10 Sep 2003 15:31:14 -0700, robsignals wrote in : detection relays, connected via 1,200:1 transformer, are rated 1Amp or 5Amp with a wide ranging multiplier, 5A was specified but 1A installed They were carried out but I guess those engineers assumed they had been handed over correctly installed equipment and never thought to check the relay rating, pity they aren't brightly colour coded. Given that there appear to be only two different ratings, an obvious question is, "Why not?" The cost of producing the item? Perhaps they aren't made? You'd hope that the maintenance engineers actually bothered to read things. Perhaps if the correct colour code was yellow they might stuff a banana in by mistake. The company my late father worked for made various control components for applications such as petrochemical plants, nuclear power-stations, oil-refineries etc. The components were colour-coded as to their intended use/ratings. On one occasion, the wrong component got fitted, which caused a major shutdown which then resulted in a significant lawsuit [this was in the USA back in the 1970s]. "It should have been made obvious by colour-coding that the wrong unit was fitted" said the refinery-company's lawyers. "The units are colour-coded according to use and rating" my father's company replied. "The fitter who fitted it is colour-blind" admitted the refinery operators after some days of the trial. Oops! -PeteL. |
#16
![]() |
|||
|
|||
![]()
robsignals said:
...I guess those engineers assumed they had been handed over correctly installed equipment and never thought to check the relay rating, pity they aren't brightly colour coded. Simulating real life faults is simply not possible or wise. Faults don't seem to be the issue. If the line went into overload protection at a fraction of what it should have done, a simple test of the line during commissioning (at 50% of rating) would have shown this. -- ============================================= Chris Game chrisgame@!yahoo!dotcodotuk ============================================= |
#17
![]() |
|||
|
|||
![]()
PJML said:
"The fitter who fitted it is colour-blind" admitted the refinery operators after some days of the trial. A classic - and one of the things quality auditors are trained to look out for. -- ============================================= Chris Game chrisgame@!yahoo!dotcodotuk ============================================= |
#18
![]() |
|||
|
|||
![]()
robsignals said:
The risk of a second fault on that circuit during this time is estimated at 1:40,000 though that doesn't apply here with the system wrongly set-up. You mean that was the calculated failure probablity ignoring the protection system? Some of this seems fairly elementary - I know this is easy to say with hindsight - but are the electricity supplies really this badly managed? -- ============================================= Chris Game chrisgame@!yahoo!dotcodotuk ============================================= |
#19
![]() |
|||
|
|||
![]()
On 10 Sep 2003 15:31:14 -0700, robsignals wrote:
Wanderer wrote in message . .. snip On any interconnected system, the National Grid being a prime example, events are by definition related. Bad choice of words on your part, I think.How can a lightning strike in the west country and a 3rd party cable damage that happened to occur at more or less the same time in the west midland be related? No, that may never have happened, but I give it as an example of the flaw in your argument. This incident was caused by a classic very simple installation 'cock-up' made 2 years ago and not discovered or exposed since; system design, configuration and incident response were correct and supplies would have been securely maintained otherwise. Not true. Somewhere between design, configuration and commisioning a current multiplier was wrongly set, and was not picked up by testing procedures that should have picked it up. snipped the actual details, read with interest, but there seem to be some notable gaps that raise even more questions [1] Yes. Knowing the very strict and thorough commisioning and testing procedures that once were enforced, one is left wondering whether corners have been cut since privatisation. They were carried out but I guess those engineers assumed they had been handed over correctly installed equipment and never thought to check the relay rating, pity they aren't brightly colour coded. Simulating real life faults is simply not possible or wise. Paragraph 177 in the report is quite explicit about the procedures used to commission the protection. I would not fault them as written. Certainly the responsibility for returning a circuit to commision in good and proper order rests *exclusively* with the guys carrying out the work. Reading the full report my impression is of a well run and financed operation not obviously damaged by privatisation with London area investment running at £50m pa. Ironically the duplicate circuit, Wimbledon - New Cross No.1, is out from 1/7 to 28/9 for upgrade and refurb. Lessons have been, painfully, learnt and the relay error is not likely to happen again. All 45,000 are being checked (none found after 9,000). I would say the system is now secure I don't share your confidence. The report paints a picture of a calm and ordered working environment that almost certainly did exist two or three decades ago. I suspect those working for NGT might have some difficulty in recognising this environment today. building extra lines would be very expensive. The LT loss of supply is rather laid on EDF, the London distribution operator, who chose to operate their Wimbledon 132kV Substation in a way that resulted in LT and others losing supply when the Grid was able to maintain the full load without interuption, and should have reconnected LT in a couple of mins at most. I get the impression there was only one engineer in their Control who didn't know what hit him... Unlikely if they operate a centralised control system. But..... [1] The gaps:- It would have been nice to see an actual schematic of the network at Hurst s/s. They have three supergrid t/frs on site. I'm guessing that each would almost certainly be independently controlled, and consequently capable of isolation, by circuit breakers on the hv and lv sides of the t/fr. Buchholz alarms are usually t/fr specific in the control room, so why did the NG control engineer apparently disconect the incoming circuit and not isolate the tranformer indicating the alarm? If this had happened the overload situation would not have occured. It would also be interesting to compare areas of responsibility and manning levels for this part of their network now and say 25 years ago. What level of authority and/or delegation of that authority holds today compared to 25 years ago? |
#20
![]() |
|||
|
|||
![]()
On Thu, 11 Sep 2003 13:06:53 +0100, Chris Game wrote:
robsignals said: The risk of a second fault on that circuit during this time is estimated at 1:40,000 though that doesn't apply here with the system wrongly set-up. You mean that was the calculated failure probablity ignoring the protection system? Some of this seems fairly elementary - I know this is easy to say with hindsight - but are the electricity supplies really this badly managed? No, they're exceptionally well managed, as it happens. What seems to have happened here is that somewhere along the line, someone either mis-set a relay or failed to notice that a relay had been mis-set. The procedure for checking that relay appears to be well-written. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
Highway or the Myway? A new Code for light relief | London Transport | |||
There are more information there | London Transport | |||
OT; Sewer Gas powered Gas light! | London Transport | |||
LURS meeting tonight: Docklands Light Railway Capacity Enhancement | London Transport | |||
London Buses - they got a special on light bulbs or something? | London Transport |